EMKoper
Member II
First, I am an engineer and I am good at multiplying units, but understanding the battery "20 AH Rate" and using that information to size a solar trickle charger (non-regulated) has me a little perplexed. Clarity is desired ....
My 3 battery bank is 2x DC31DT house batteries and 1x DP27 Starter ... I would like to understand the size of a solar unit to trickle charge the full bank. From the Deka website:
*** Note: if you are reading this, the correct approach was not 3%, but 0.3% ... please keep reading! ***
OK ... I have read that a trickle charge is supposed to be 3% of the amp capacity (more that below) .. but I am a little lost in the "20 AH Rate" definition (sorry, engineering confusion, rate is "something"/"something" not "something"*"something" but don't let me overthink this, too) ...
The DP27 "20 AH Rate" is 80 ... I think this means that it have expel 4 amps per hour under a load that totally depletes the battery in a 20 hour period. So this would be an 80 AH battery... right?
The 2x DC31DTs are a rating of 105 ... which means they are each 5 amps per hour under load, so each is about a 100 AH battery ...
So, in total, I have ... (drum roll) .... 280 AH with a full charge by the "20 AH Rate" standard ... this seems basically reasonable but I have never pressed the test first hand on the true working capacity of these batteries.
I have this book, "Sailboat Electronics Simplified" by Casey (page 123) and it says that a maintenance current is 3% of the Amp-Hour Capacity which says I need 8.4 amp for maintenance (280 AH * 3%) or (based on their formula, amps*16V) 134 Watts of solar power to maintain charge under idle conditions. (never mind that the units don't multiple/divide correctly in their equation).
This seems unreasonable ... too high ... too much for simple maintaining a charge ... what am I missing?
My 3 battery bank is 2x DC31DT house batteries and 1x DP27 Starter ... I would like to understand the size of a solar unit to trickle charge the full bank. From the Deka website:
*** Note: if you are reading this, the correct approach was not 3%, but 0.3% ... please keep reading! ***
OK ... I have read that a trickle charge is supposed to be 3% of the amp capacity (more that below) .. but I am a little lost in the "20 AH Rate" definition (sorry, engineering confusion, rate is "something"/"something" not "something"*"something" but don't let me overthink this, too) ...
The DP27 "20 AH Rate" is 80 ... I think this means that it have expel 4 amps per hour under a load that totally depletes the battery in a 20 hour period. So this would be an 80 AH battery... right?
The 2x DC31DTs are a rating of 105 ... which means they are each 5 amps per hour under load, so each is about a 100 AH battery ...
So, in total, I have ... (drum roll) .... 280 AH with a full charge by the "20 AH Rate" standard ... this seems basically reasonable but I have never pressed the test first hand on the true working capacity of these batteries.
I have this book, "Sailboat Electronics Simplified" by Casey (page 123) and it says that a maintenance current is 3% of the Amp-Hour Capacity which says I need 8.4 amp for maintenance (280 AH * 3%) or (based on their formula, amps*16V) 134 Watts of solar power to maintain charge under idle conditions. (never mind that the units don't multiple/divide correctly in their equation).
This seems unreasonable ... too high ... too much for simple maintaining a charge ... what am I missing?